208v to 120v Step-Down Auto Transfer Switch
Anybody have any luck finding or using a step-down Auto Transfer Switch that goes from 208v to 120v?
There are a few items on one of our racks that are 120v and I'd like to get them on redundant UPS' and this is the only way I can think of how to do it. All the UPS' in this room are 208v in and out.
Thanks
There are a few items on one of our racks that are 120v and I'd like to get them on redundant UPS' and this is the only way I can think of how to do it. All the UPS' in this room are 208v in and out.
Thanks
Current: CISM, CISA, CISSP, SSCP, GCIH, GCWN, C|EH, VCP5-DCV, VCP5-DT, CCNA Sec, CCNA R&S, CCENT, NPP, CASP, CSA+, Security+, Linux+, Network+, Project+, A+, ITIL v3 F, MCSA Server 2012 (70-410, 70-411, 74-409), 98-349, 98-361, 1D0-610, 1D0-541, 1D0-520
In Progress: Not sure...
In Progress: Not sure...
Comments
-
gc8dc95 Member Posts: 206 ■■□□□□□□□□Are they WYE 208V 3PH? You could just pull a single phase and neutral for 120V, if thats the case. Be sure to balance the load.
If you need a single phase solution you will need a transformer. Preferably before a 120V UPS, but you could do it after a 208V UPS if needed. Just beware that the isolation and cleaning properties of the UPS could be affected by doing it this way. -
joelsfood Member Posts: 1,027 ■■■■■■□□□□I used one of these for a client who had 208v, and colo wanted 500/mo to drop 120v feed for the 2-3 items that needed it.
Buy APC Step-Down Transformer RM 2U 208V IN 120V OUT; w/5-20 Receptacles - Technical Specifications and Information | APC